So back from another weekend and more from my "little Tremor projects" with some quick and fun updates:
After the boy's tennis tournament Saturday morning, we went back to work on this experiment and the outdoor settings couldn't have been any better.
This weekend, we had record temperatures for this time of the year of maximum daily highs of 116F but more like an outdoor temperature feel of 121+ ambient temperature - I thought this was simply perfect for extreme weather testing.
We used this opportunity to head out and simulate how we would be using the anderson connectors in the real world.
First testing went suprisingly good for about 15 minutes, running the hammer on a concrete washout pit with no ill-effects until the inverter abruptly shuts off.
First thing we look at is the breaker relay under hood (the engine hood was open the entire time receiving all them bright UV rays and we're still not sure if this was good or bad?), to reset the breaker and it would not reset. I did not think about taking a digital thermometer with me but by hand and feel, the wiring, along with the connectors all felt normal -- nothing indicated or showed signs of overheating all the way to the hammer. The hammer casing did feel hot but that was to be expected after running it non-stop in this extreme weather, breaking concrete.
What did not feel normal was the relay itself and the terminal lead to the postive post on the battery so we decided to pull this and run it direct to see if there were any other damages or issues along the line, pun intended.
Luckily, the inverter turns back on with no problem and we give it another 15 minute run, constantly checking all cables, plugs, extension cord along with feel by touch of all these components and connections. Nothing to be panicked about about but what we did noticed was the battery voltage increased by 0.6 volts reaching 10.7 from the previous 10.1 as seen in the image above.
We collect our data and decide to head home.
Testing time was done at 3pm, running max AC in the cab, engine idle set to 1,500 RPM.
We head home and begin to process what we just observed. At the same time we grab the relay and of course its back to normal temperature by now, but what do you know? It's back to functioning again but it just feels different. The reset tab doesn't seem to click as smoothly as when new but its cooperating.
For a 300amp at $15 a pop, what more can you expect so we make our quest to find something sturdier perhaps heavier duty or even more amps for further testing
On a late Saturday evening, nothing was found and what we gathered from asking a few folks around - those type of relays have proven to be simply unreliable over the years for big loads (oxymoro?) and even in going with higher quality ones, their life span won't exceed a year tops. Back to the drawing board....
Unsure if its really the AMP draw or the relay itself, we come across a used solenoid I had in the tool box as mentioned by
@Phil314 so we wire it in, the next day.
This time, we decide to run the hammer under the shade (along with the truck), using the solenoid in the same set up as the relay breaker, and she didn't blink one bit. The time of the day was roughly the same, along with the ambient temperature, and all other variables were kept constant. After a good 30 minute trial, we give it some rest and head out to the open sun to compare differences. Suprisingly enough, after another whopping 30 minutes of constant hammering, everything was operating under what we consider normal conditions and no interruptions from any of our components.
As a last test to this run, we wanted to find out just how bad the relay had been damaged so we decide to wire but only as a switch to the solenoid to find out if it would trip it or even allow the circuit to open the solenoid and feed power to the connection points. Much to our surprise, the relay worked as inteded, using it
only as a switch to open the solenoid as we feel the relay was weakend by the heat during our first test run.
The only other thing we wanted to test was the rear winch which we feel would signficantly pull more draw than the hammer during continous use but it was just too darn hot out and it was getting late plus we were exhausted at this point.
Conclusion from these observations:
The current cable run will operate our power tools for the time being and possibly even the winch a time or two but the cable will drastically loose intergrity with each use from the heat produced by these loads. It will likely get hotter quicker, to the point where it will not resist big loads such as yesterday's trial for long periods of time and I don't want to know what can happen next.
With the cooler months quickly approaching us (or so I hope), it will certainly help prolong the cable's life but likely won't withstand another summer's brutal heat and full power loads. I will keep a good eye on the cable's feel by hand to observe any "softness" of the insulation protection and if I observe the cable simply starts to feel too "soft", I will know its time to replace it for something better.
As already determined, only a good 2/0 or 4/0 cable will resist these extreme temperatures safely and more appropriately especially over time, all due to the length of the run and under these power loads.
Another thing I learned was, those manual circuit breakers are simply not realiable especially for heavy electrical loads. I was advised to use any of what you guys have mentioned or the ones commonly used in today's industry is the ANM type which can go up to 500AMPs.