Follow-Up on this article: After searching the Amerex site and some sleuthing, here's what I found.
There are several factors that need to be considered to determine a "safe" storage of the extinguisher. Here's the short version based on the Amerex model B417 2.5 lb. dry chemical ABC:
1. Bottle construction: The bottle will have a "tested" pressure and date usually stamped on the bottom of the bottle. Mine is 40 BAR or approximately 580 PSI. Some extinguishers will also have the weight of the bottle and total weight of the chemical + bottle on a label.
2. The ABC dry chemical (perhaps others) operate at 240 PSI. (DOT specification) This pressure would have to rise well above the 580 PSI to be considered dangerous of explosion. The gauge has a max marking of 400 PSI. If the pressure was to rise past this indicator, it could be considered "dangerous".
3. Another thing to consider is the type of nozzle. Plastic may not be as robust as an all-metal version. (The Amerex B417 is all metal (aluminum) except the gauge)
4. The chemical "thermal decomposition" is 100-120 C. (212-248F) This is the point where the chemical compound can change and jeopardies its effectiveness. The chemical is not dangerous as to explosion. (Might make a mess if it goes off though.)
5. The Amerex MSDS (safety data sheet) indicates storage as: Storage P410+403 *- Protect from sunlight. Store in well-ventilated place. *if under pressure.
6. This bottle meets DOT criteria tested to 585 PSI.
7. Use valid for -65 to 120F. (Use does not indicate the pressure it will withstand but the "tested to" 585 PSI should be a clue.)
8. Kidde has a different way to specify this:
What Temperature Can You Store a Fire Extinguisher?
Kidde fire extinguishers should be stored in temperatures ranging from -40 degrees to 120 degrees Fahrenheit. Fire extinguishers stored below -40 degrees Fahrenheit may result in the extinguisher's valve or hose cracking. At temperatures above 120 degrees, the fire extinguisher will still function, but the discharge time may be a little shorter than the 9 to 10 seconds required by
Underwriters Laboratories UL.
So bottom line, you should have no problems in most all circumstances with the extinguisher stored in your vehicle. Just keep an eye on the gauge in extreme temperatures exceeding 120F.