Who on here is a solar wizard/expert?

Generally, the junction box will help the solar play well with other power sources (generator, shore power, etc)
But it sounds like it's already 'bypassed' the junction box and goes directly to the batteries based on your previous response.

Yes, inline fuse or mini circuit breaker between controller and batteries.

Ok, I've just started drinking, so don't trust a word I say after this post.
I'll take a picture of the junction box in the morning and you'll see what I want to bypass. It's sad to say the least 🤣
 
That means there is no real good way to connect them all up and get 600w.

Just drop in another MPPT....done.

I say this as I did my own "solar experiment" with a solar generator and solar panels. So with one panel plugged on to the solar generator MPPT I could get good charging. Then as the solar generator had a second input for a MPPT, I bought a second MPPT. I bought some older home version solar panels, swapped out the connectors to fit the current style, then hooked the panels to the MPPT. Damn...works like a charm running two different sets of panels into the same solar generator. Best thing is to write down all your specs, plan the system out on paper, get the numbers where you want them. Then get ready for the fun part.

I'd leave whatever panel is already installed. You will want more power (input capacity) down the road.
 
I had two Redarc BCDC1250 installed and that did the trick for me from a DC/DC charging perspective and solar as well. My new rig has two different Victron MPPT controllers installed. One for the roof 800W and one for the 3 external panels I can connect.
 
1000003797.webp
1000003798.webp
1000003799.webp
1000003800.webp
1000003801.webp
1000003802.webp
1000003803.webp

Here's a few pictures. First is the awesome junction box that is next on my list of fixes to the RV. Then a few pics of the adjustments I made to the factory solar panel. And the "finished for now" setup. Going to have to get a better controller before I add panels. Mainly because I figured out it'll only handle 400w max 🤷

1) fix junction nest.. I mean box
2) upgrade battery bank
3) upgrade panels and system
 
Here's a few pictures. First is the awesome junction box that is next on my list of fixes to the RV. Then a few pics of the adjustments I made to the factory solar panel. And the "finished for now" setup. Going to have to get a better controller before I add panels. Mainly because I figured out it'll only handle 400w max 🤷

1) fix junction nest.. I mean box
2) upgrade battery bank
3) upgrade panels and system

Looks like you're making good progress.
Maybe the factory was trying to make up for the missing controller by giving you extra sealant, lol. 😂

Yes, given your current controller, you are limited to 400watts.
If you want more, you'll need a better MPPT controller and either more 100w panels that match or get a set of bigger panels.
You've probably got enough roof space to do either.

That junction box is a crime. It literally is a steel junction box. Not even really sealed against the weather.
 
Looks like you're making good progress.
Maybe the factory was trying to make up for the missing controller by giving you extra sealant, lol. 😂

Yes, given your current controller, you are limited to 400watts.
If you want more, you'll need a better MPPT controller and either more 100w panels that match or get a set of bigger panels.
You've probably got enough roof space to do either.

That junction box is a crime. It literally is a steel junction box. Not even really sealed against the weather.
I have a good bit of space. Kinda broken up by the 50 vents and skylights 🤣. Yeah, that junction box is insane, and it seems like you'd have to be an elf to even work the wires into it like they did 🤷. But, for 26k when my 18' trailer cost me 22k, I can deal with the stupidity😉🤣🤣

They also had an automotive inline 10a fuse running an even smaller wire than the "zipcord"(which was smaller than the solar wire I ran to the battery/should've been ran from the panel) 🤦. I blew that cutting the wire loop 🤣🤣. So, I will definitely be rerunning new wire when I upgrade the roof panels 👍
 
Going to have to get a better controller before I add panels. Mainly because I figured out it'll only handle 400w max 🤷

1) fix junction nest.. I mean box
2) upgrade battery bank
3) upgrade panels and system
It definitely looks like someone added the solar panel after the fact and spliced it into the main power cable from the battery box without a charge controller. What a monkey.

Regarding the solar controller - while of course I recommend MPPT over PWM all day every day, it's not critical to change right now. You are unlikely to reach 400W for more than an hour a day, and "overpaneling" is not a bad idea since you rarely hit max power. You will not hurt the charge controller by connecting more panels to it as long as you don't exceed the 50VDC max. It will only draw enough power to satisfy its max output.

I would sort out all your wiring, sized for future growth, then replace the charge controller after you get everything working. To be honest 400W is all you need unless you want to make the jump to lithium and a high power inverter.
 
It definitely looks like someone added the solar panel after the fact and spliced it into the main power cable from the battery box without a charge controller. What a monkey.

Regarding the solar controller - while of course I recommend MPPT over PWM all day every day, it's not critical to change right now. You are unlikely to reach 400W for more than an hour a day, and "overpaneling" is not a bad idea since you rarely hit max power. You will not hurt the charge controller by connecting more panels to it as long as you don't exceed the 50VDC max. It will only draw enough power to satisfy its max output.

I would sort out all your wiring, sized for future growth, then replace the charge controller after you get everything working. To be honest 400W is all you need unless you want to make the jump to lithium and a high power inverter.
I doubt I'll ever boondock in this camper anyway. Mostly just want to be able to disconnect from shore power(my house). As of now it sits blocking my front door view 🤣 but, I might like to sit it on my property and be able to keep the refrigerator and lights/TV running during the day as a sort of hunting cabin until I can get the property tied into main power or a solar "farm". I'll probably end up trying to suss out the 4 other panels on the camper and add a few batteries and if it ends up too much for the controller, then I'll upgrade 👍
 
Be cafeful running the fridge it will suck the batteries in no time. We use propane for the fridge and hot water heater, way easier on the system. If you’re setting it on property for occasional trips I vote big battery bank and should it should be all charged up and ready when you use it.
 
Be cafeful running the fridge it will suck the batteries in no time. We use propane for the fridge and hot water heater, way easier on the system. If you’re setting it on property for occasional trips I vote big battery bank and should it should be all charged up and ready when you use it.
I'll probably get a dual fuel generator for the fridge then. I have the propane on demand water heater. (That thing was/is a bastard if you can't get the water pressure up 🤦 Had to get a different shower head to get it to run, even supplementing pressure with the fresh tank)
 
1000000982.webp

For my solar wizards:
What is the smallest solar generator I could get to run this pump?
It's about a 40ish foot well
I would like to be able to run a light bulb constantly during the winter if possible to keep it from freezing. (probably only a few actual freezing days/nights. I could probably just insulate it well and it would be fine 🤷)
Not for constant use, just here and there to fill drums, wash hands, or for when we have a fire pit going.
 
@Blade420Play This might be an odd take on it, but seeing as you would need to provide heat to not just the pump, but all lines to/from the pump that are exposed to ambient air temperature and are above ground, I would winterize that pump and all lines with RV antifreeze for the few days of below freezing temps (only normally 3 dollars a gallon or so at Walmart.) Just run the pump to flush out the antifreeze when you want to use the pump

For the solar generator, the pump says 7Amps of input, that is 840 Watts at 120Volts. Any small solar generator that can run with 1000 watt continuous load with do well. I'm partial to the units from the brands EcoFlow, Goal Zero, and Anker for both price and performance.
 
View attachment 188322
For my solar wizards:
What is the smallest solar generator I could get to run this pump?
It's about a 40ish foot well
I would like to be able to run a light bulb constantly during the winter if possible to keep it from freezing. (probably only a few actual freezing days/nights. I could probably just insulate it well and it would be fine 🤷)
Not for constant use, just here and there to fill drums, wash hands, or for when we have a fire pit going.
Well, Amps X Volts = Watts so….

7 Amps X 110V = 770W…

BUT 1 hp is 746W and you’ve got 1.5hp there so I’d say that’s 1200W. General rule is you can’t run anything continuously at more that 80% draw so 1200W/ .80 =1,500 W

1500W inverter should run that just fine. Add a 100W light bulb you’ll still probably be ok.

So you need a 1500W or more inverter on a solar generator.

Now if you’d like to know how long it can run or how large a battery bank or solar you need I can do that for you but to run that pump you need about 12.5A. I’m not sure why that pump says 7A but that doesn’t seem very realistic to me.

Don’t you live in SC??? How cold could you be!?
 
Well, Amps X Volts = Watts so….

7 Amps X 110V = 770W…

BUT 1 hp is 746W and you’ve got 1.5hp there so I’d say that’s 1200W. General rule is you can’t run anything continuously at more that 80% draw so 1200W/ .80 =1,500 W

1500W inverter should run that just fine. Add a 100W light bulb you’ll still probably be ok.

So you need a 1500W or more inverter on a solar generator.

Now if you’d like to know how long it can run or how large a battery bank or solar you need I can do that for you but to run that pump you need about 12.5A. I’m not sure why that pump says 7A but that doesn’t seem very realistic to me.

Don’t you live in SC??? How cold could you be!?
Cheap Asian pump 🤷🤣
 
View attachment 188322
For my solar wizards:
What is the smallest solar generator I could get to run this pump?
It's about a 40ish foot well
I would like to be able to run a light bulb constantly during the winter if possible to keep it from freezing. (probably only a few actual freezing days/nights. I could probably just insulate it well and it would be fine 🤷)
Not for constant use, just here and there to fill drums, wash hands, or for when we have a fire pit going.
If you are just running it sporadically and not continuous for any appreciable amount of time it will be a matter of the startup load. Judging by the 1.2KW rating you'll probably need something 2K or higher. Some power stations have higher instantaneous output for handling startup loads. The Ecoflow I was looking at, for instance, can support up to 2.2KW:

 
I’m not sure why that pump says 7A but that doesn’t seem very realistic to me.
Agree. I would believe the 7A if it was a 220V system. The other line on the tag says it's a 1.2KW pump. You can't get that from 110V and 7A. Friction works the other way.
 
Agree. I would believe the 7A if it was a 220V system. The other line on the tag says it's a 1.2KW pump. You can't get that from 110V and 7A. Friction works the other way.
My thoughts exactly
 