I know this is a truck forum, but I know y’all are a wealth of knowledge in other areas and I would love for a quick glance at a problem I’m having with my furnace. See if I’m missing anything obvious or if I should call in a tech.

Video of what’s happening. This is one cycle, but the furnace will repeat this 5 or so times until it locks out for an hour.



Notes:
  • Rattling noise before the burners go out is consistent.
  • Amount of time between ignition and the burners going out is fairly consistent. I haven’t explicitly timed it, but there isn’t a massive variance.
  • I have not been able to pinpoint the source of the rattle.
  • I have tried cleaning the flame sensor, as well as replacing it (they’re cheap) with no observed change in behavior.
  • There is a light indicating the presence of flame, and it appears to be responding perfectly consistently with the burners, further indicating the flame sensor is working correctly.
  • Filters have been replaced recently and are clean. Problem persists with filters removed.
Thankfully the furnace stopped working on the first warm weekend of the year, and I have a gas fireplace to keep me going so I’m not needing to pay after-hour rates for a tech.

Thank you in advance!
 
Last edited:
Might be a bad thermocouple. It will shut off the burners if it isn't detecting that there's a temperature rise. Thermocouples don't rattle though, so that's likely a relay or two clicking.
 
I don't think my furnace has a thermocouple. It's electric ignition (there's an igniter right in the path of one of the burners, and it's reliably igniting).

Good point on the relays being a likely source of the rattling, though.
 
There should be a computer board somewhere that has a couple leds or maybe even a display of some type (some show 2 digits) to give status and error codes. Location varies but sometime they are below where the blower/fan is. Sometimes they have a cover you have to remove.

If you can find this board with the leds or screen and get the error code that will likely let you know what’s broke and guide you in the right direction.

Make and model of the furnace will help too.
 
I don't think my furnace has a thermocouple. It's electric ignition (there's an igniter right in the path of one of the burners, and it's reliably igniting).

Good point on the relays being a likely source of the rattling, though.
It still needs a way to detect temperature, which the ignitor can't do.

Definitely see if there's an error code readout like @Himni suggested.
 
These are my top guesses I got from a quick search.

  1. Faulty pressure switch – Adequate air flow through the draft inducer fan motor housing will cause the pressure switch to close, allowing the ignition process to continue. A faulty pressure switch may be unable to close, stalling the ignition process and shutting off the furnace. You can use a multimeterto determine if there is continuity, a continuous electrical path, present in the switch, provided the switch is connected to the furnace and the draft inducer fan motor is running. If there is no electrical continuity, you’ll know the switch has failed and will need to be replaced.
  2. Defective control board – The control board regulates the power supply to all of the furnace components. A defective control board may not send voltage to the ignition system, causing the furnace to shut off after a few minutes. While a control board can be difficult to test, you can inspect the board for any burn marks or evidence of a shorted component.
  3. Faulty draft inducer fan motor – The draft inducer fan motor draws air into the heat exchanger and then exhausts that air out of the flue. Since proper air flow is required for the pressure switch to close and the ignition process to begin, a faulty draft inducer fan motor unable to maintain proper air flow can stall the ignition process and shut the furnace off after a few minutes. You should listen to the motor just as the furnace starts up. Are you hearing a buzzing, grinding, or screeching sound? Then it’s likely the motor bearings are failing and you will probably need to install a new draft inducer fan motor.
  4. Air flow problem – In order to continue running, the furnace requires sufficient air flow through the burner assembly. Poor air flow is often the result of insufficient ventilation or a restricted inlet or exhaust vent. Make sure the furnace is in a properly ventilated location free of boxes or other items placed near the furnace cabinet and check that the vents are clear of obstructions.

It still needs a way to detect temperature, which the ignitor can't do.

Definitely see if there's an error code readout like @Himni suggested.
He said he replaced the flame sensor which would be the thermocouple if he replaced what I think he did.

@ccw when you say flame sensor you are talking about the little metal tip that sits in the flame, usually by/in the pilot light/ignitor?
 
There should be a computer board somewhere that has a couple leds or maybe even a display of some type (some show 2 digits) to give status and error codes. Location varies but sometime they are below where the blower/fan is. Sometimes they have a cover you have to remove.

If you can find this board with the leds or screen and get the error code that will likely let you know what’s broke and guide you in the right direction.

Make and model of the furnace will help too.
Ah I should have called that part out originally: no helpful error codes. Only error code is indicating the furnace is in lockout (once it's in lockout). Nothing about why it's going into lockout. I logically know it's going into lockout because it's failing to sustain a flame too many times.

Furnace is a Rheem RGLH-07EAMGR, installed in 2001 (original furnace for the house).

It still needs a way to detect temperature, which the ignitor can't do.

Definitely see if there's an error code readout like @Himni suggested.
He said he replaced the flame sensor which would be the thermocouple if he replaced what I think he did.

@ccw when you say flame sensor you are talking about the little metal tip that sits in the flame, usually by/in the pilot light/ignitor?
Correct. The thing that tells the furnace the burners are actually burning. So ya, I guess it's generically a thermocouple but has a specific name in this case. :)

Is the blower fan motor even working?
Yes, blower fan turns on the first attempt after the burners successfully ignite. Verified both by ear and by feeling the vents.

These are my top guesses I got from a quick search.
Hmm. Not the pressure switch; replaced that a year or two ago and the symptoms were different, plus there was an error code for it. Inducer fan motor is definitely working; I can visually see it as well as hear it. Airflow and control board...that might be where I need a tech. I don't know how I would test those.

Flux capacitor isn’t set to 88 mph. See it all the time….
See! I knew it would be simple! :P
 
Is the blower fan motor even working?
The blower fan to circulate air through ducts and house usually won’t kick on until the heat exchanger has gotten hot enough and it doesn’t look like it stays on long enough for that to happen. The little black square with 2 wires is a thermocouples that kicks the blower on.

IMG_1796.jpeg


ETA: @ccw about how long until it kicks off after ignition? 10 second or minutes? If it’s short like less than like 30 seconds I have any idea for you to try.

Not having experience/lived with your furnace I can’t say for certain but it seems like the blower is kicking on too soon but I don’t know if that would cause this issue. Can you recall in the past if it ignited and how long before the blower kicked in?

You could try unplugging one wire to the thermocouple in the yellow box and have it fire up and wait like 30 seconds and plug it back in and see if it stays lit. Don’t leave it unplugged and ignited too long or you could crack the heat exchanger if the blower is off. If the blower doesn’t turn on until you plug it back in it could be the bad part.
 
  • Like
Reactions: ccw
Can you move your phone on top of the solenoid pack to confirm that's the source of the clicking noise?
Was focused on finding the noise (rather than filming) and quite confident it’s coming from the gas valve. Like it’s failing to stay open, and fluttering before closing completely.

Got that from touching the gas valve and various relays on the control board while the noise happened so I could “feel” the sound.

I don’t know whether that’s because the valve itself is faulty or whatever signal is telling it to stay open is flaking out for whatever reason. Leaning towards signal?
 
Was focused on finding the noise (rather than filming) and quite confident it’s coming from the gas valve. Like it’s failing to stay open, and fluttering before closing completely.

Got that from touching the gas valve and various relays on the control board while the noise happened so I could “feel” the sound.

I don’t know whether that’s because the valve itself is faulty or whatever signal is telling it to stay open is flaking out for whatever reason. Leaning towards signal?
If the flyback/snubber diode failed (should be on the control board), then it could cause a fluttering valve for sure as the valve coil switches off.
 
The blower fan to circulate air through ducts and house usually won’t kick on until the heat exchanger has gotten hot enough and it doesn’t look like it stays on long enough for that to happen. The little black square with 2 wires is a thermocouples that kicks the blower on.

View attachment 149432

ETA: @ccw about how long until it kicks off after ignition? 10 second or minutes? If it’s short like less than like 30 seconds I have any idea for you to try.

Not having experience/lived with your furnace I can’t say for certain but it seems like the blower is kicking on too soon but I don’t know if that would cause this issue. Can you recall in the past if it ignited and how long before the blower kicked in?

You could try unplugging one wire to the thermocouple in the yellow box and have it fire up and wait like 30 seconds and plug it back in and see if it stays lit. Don’t leave it unplugged and ignited too long or you could crack the heat exchanger if the blower is off. If the blower doesn’t turn on until you plug it back in it could be the bad part.
I can’t recall exactly. I feel like it’s behaving fairly normal in that regard?

Ok, exact steps I’m seeing with times from the last run (there’s some variance):
1. T=0 Inducer turns on.
2. T=38 Igniter starts.
3. T=41 Ignition succeeds, burners are lit.
4. T=60 Burners go out.
5. T=61 Blower fan turns on.

The blower stays on for all future ignition attempts until lockout.

Given that I think I was mistaken before about the blower behavior. Now that I have the panel off and am manually holding down the switch to turn the furnace on I’m getting a much better idea of the cycle. Especially that initial attempt.
 
If the flyback/snubber diode failed (should be on the control board), then it could cause a fluttering valve for sure as the valve coil switches off.
Interesting. I suppose there’s not an easy way to test that, eh? I do have a multimeter, but no oscilloscope.
 
If the flyback/snubber diode failed (should be on the control board), then it could cause a fluttering valve for sure as the valve coil switches off.
It’s also crossed my mind that I try a new board. Can get one for $250 on Amazon and doesn’t seem terribly difficult to switch everything over.
 
Interesting. I suppose there’s not an easy way to test that, eh? I do have a multimeter, but no oscilloscope.
You can test a diode on the board (unplug all power to and from the board).

Use the diode function on your multimeter (or continuity tone mode).
 
  • Like
Reactions: ccw
You can test a diode on the board (unplug all power to and from the board).

Use the diode function on your multimeter (or continuity tone mode).
Ok that’s going to take a bit. Either I need to find a circuit diagram or spend a while testing all the diodes. 20 of them or more on the furnace.

There’s this interesting component on top of the blower and it’s connected to the gas valve (a blue wire and a yellow wire).

image.webp
 
Ok that’s going to take a bit. Either I need to find a circuit diagram or spend a while testing all the diodes. 20 of them or more on the furnace.

There’s this interesting component on top of the blower and it’s connected to the gas valve (a blue wire and a yellow wire).

View attachment 149442
That may be a fan limit switch. Basically, if it gets too hot, it will shut the gas off (for the scenario of the blower not working and moving air)

Worth checking that as well!
 
  • Like
Reactions: ccw