I had a friend come by to do some electrical work for me. I bought the Predator 9,500 inverter generator to run my house in case of a power outage. I wanted a Generac generator but in my town you need a permit and i didn't want to go that route so i got the predator for 2,000$.
I have a 50amp/30amp/20amp box set up for a RV. I watched a UTibe video, with a guy that ran this Predator inverter into his 30amp box and instead of getting power from it the inverter powered every thing. You need to shut your main breaker to the house off. I did need to have a double male extension cord which we made. My buddy added a 4 prong 30amp connection to my outside RV setup.
Pretty freakin COOL and really cheap way to have a back up to power your house. I needed to mark what breakers i wanted on in my house to be able to power as much of the house that needed to be powered.
My friend who built my shed and ran the electric to my RV box and shed was over, he looked at the stairs to my deck and said they are ready to fall. The last owner built the deck completely wrong. Thats another story.

8CC49C50-5131-4025-8337-B29699C96E0E.png
09F8B9DC-5B78-4440-82A6-4D0D52C42A05.jpeg
42137BC4-ADCE-4492-B327-3AADC0829C8C.jpeg
B11A9B09-F297-49A0-A4FB-F25CEEF254EE.jpeg
3647F0A0-CEA9-4E59-804D-8EA435DB1D1D.jpeg

 
I have a 30A hook up outside right by my meter that I use when our power goes out. It works great and we can do everything but our AC … well, multiple freezers, fans, lights, etc. I’ve got a 8,500 frame generator that I use for that.
And should say that the receptacle has a Male plug, so a standard M/F cable is used.

I’ve got a little 2000W inverter that I use if we are goign to be down for a little while and I just jack it right into one of the 110 outlets under cover on our porch. IT will power enough to keep us comfortable for a few hours. For this one I have a M/M cable that I made up ... just be careful not to touch the wrong end.
 
Ah, the no-no plug.

Make sure you have an interlock device on your main panel, so that there's no chance of back-feeding to the grid when you are on generator power. Makes it super fucking dangerous when there are downed lines and you're suddenly feeding 50A to them.
 
What’s the forbidden plug?
A Male to Male extension cable. Ends up hot and easy to sting yourself with if plugged into a live circuit. Also allows you to back feed into your house, and power grid, by plugging into one of your available wall outlets. If you don’t have your main shut off you will energize the lines outside you home .. that linemen may be working on and that *should be* dead because of the power outage that has called them out to your area.
 
Donny,
What a nice clean install it looks fantastic! One step closer brother to plugging in your dream RV.
We went a little different route as my 200 amp panel is right behind the 30 amp boxes in this photo. We have a lock out switch or interlock so the Gen cannot backfeed and kill a lineman.
The smaller box on the right is my 30 amp out let for my 10 gauge extension cord to our camper 30 amp outlet. The longer box on the left is where we plug in our Honda 7000is fuel injected portable gen set which powers everything we need except our 4.5 ton AC. We have ceiling fans in every room so no big deal. $325.00 install included box and 80’ 10 gauge cord. All by code.


Great looking set up you have, there is is nothing like seeing a home remodel done in such a seamless professional sweet looking appearance. πŸ‘πŸ»πŸ‘πŸ»πŸ‘ŒπŸ»
And there is nothing like Gen power when you need it!
147E1639-8D7C-4B19-A1A4-B6E6DC3CEAF3.jpeg


I installed a β€œgentent” cover to keep the rain and weather off the Gen when in operation.

B7586BF6-344E-41D0-B013-D26998D42F34.jpeg

We keep our Oliver Legacy Elite ll plugged in year round here at home. πŸ‘πŸ»
E5E57184-D67D-4302-B1E9-CD181AEF5F09.jpeg
 
Last edited:
A Male to Male extension cable. Ends up hot and easy to sting yourself with if plugged into a live circuit. Also allows you to back feed into your house, and power grid, by plugging into one of your available wall outlets. If you don’t have your main shut off you will energize the lines outside you home .. that linemen may be working on and that *should be* dead because of the power outage that has called them out to your area.
Ahhh gotcha.
 
You can get an interlock retrofit kit for your panel and an official 'inlet' device that can never be made hot via the interlock (since it has exposed terminals with no cord plugged in). Eliminates the stinger cord and still keeps things inexpensive and proper and can be done within half an hour without scrapping the other work you've already completed.

Imagine the inlet's breaker as never allowing power to flow out of it, it's only purpose is to accept power from another source while keeping any line workers and the genset safe for when power is restored. Never install an inlet without an interlock.

Interlock:
0xveU9P.jpg


Inlet:
dxT580S.jpg
 
Last edited:
You can get an interlock retrofit kit for your panel and an official 'inlet' device that can never be made hot via the interlock (since it has exposed terminals with no cord plugged in). Eliminates the stinger cord and still keeps things inexpensive and proper and can be done within half an hour without scrapping the other work you've already completed.

Imagine the inlet's breaker as never allowing power to flow out of it, it's only purpose is to accept power from another source while keeping any line workers and the genset safe for when power is restored. Never install an inlet without an interlock.
Yep, for sure an interlock switch is code. Ya dam sure don’t want to kill any lineman.
 
This is one situation where pulling permits is important, especially when the current setup can cause the death of a line worker. Recommend having permit pulled and work inspected after that interlock is added.

Besides that, please share your experience with the HF inverter, I'm curious if they've improved from the previous non-inverter gen.
 
You can get an interlock retrofit kit for your panel and an official 'inlet' device that can never be made hot via the interlock (since it has exposed terminals with no cord plugged in). Eliminates the stinger cord and still keeps things inexpensive and proper and can be done within half an hour without scrapping the other work you've already completed.

Imagine the inlet's breaker as never allowing power to flow out of it, it's only purpose is to accept power from another source while keeping any line workers and the genset safe for when power is restored. Never install an inlet without an interlock.

Interlock:
0xveU9P.jpg


Inlet:
dxT580S.jpg

Please install it the correct way like this with an inlet and interlock kit. I did this years ago and it’s cheap and easy and ensures no one can get hurt.

It’s worth a couple hundred dollars and an hour of time to ensure no one ends up dead.
 
The forbidden plug.

Not sure about your area but that's a huge fucking fine and super illegal where I live if they catch you.

Key work being catch.
I have a 30A hook up outside right by my meter that I use when our power goes out. It works great and we can do everything but our AC … well, multiple freezers, fans, lights, etc. I’ve got a 8,500 frame generator that I use for that.
And should say that the receptacle has a Male plug, so a standard M/F cable is used.

I’ve got a little 2000W inverter that I use if we are goign to be down for a little while and I just jack it right into one of the 110 outlets under cover on our porch. IT will power enough to keep us comfortable for a few hours. For this one I have a M/M cable that I made up ... just be careful not to touch the wrong end.
You can get an interlock retrofit kit for your panel and an official 'inlet' device that can never be made hot via the interlock (since it has exposed terminals with no cord plugged in). Eliminates the stinger cord and still keeps things inexpensive and proper and can be done within half an hour without scrapping the other work you've already completed.

Imagine the inlet's breaker as never allowing power to flow out of it, it's only purpose is to accept power from another source while keeping any line workers and the genset safe for when power is restored. Never install an inlet without an interlock.

Interlock:
0xveU9P.jpg


Inlet:
dxT580S.jpg
Yep, for sure an interlock switch is code. Ya dam sure don’t want to kill any lineman.
This is one situation where pulling permits is important, especially when the current setup can cause the death of a line worker. Recommend having permit pulled and work inspected after that interlock is added.

Besides that, please share your experience with the HF inverter, I'm curious if they've improved from the previous non-inverter gen.
Please install it the correct way like this with an inlet and interlock kit. I did this years ago and it’s cheap and easy and ensures no one can get hurt.

It’s worth a couple hundred dollars and an hour of time to ensure no one ends up dead.
Yeah I want it done correctly for sure. I noticed the 30 amp 4 prong and a 30 amp 3 prong coming off the generator so i asked for that 4 prong set up. But it looks like every one has the 3 prong with the inter lock. Sweet set up David and Bill. You all gave me so much info. I wish I would have asked for help or advice first. Thanks again you wise Men. πŸ‘Š πŸ‘Š πŸ‘Š πŸ™ πŸ™ πŸ™ ;)
 
Yeah I want it done correctly for sure. I noticed the 30 amp 4 prong and a 30 amp 3 prong coming off the generator so i asked for that 4 prong set up. But it looks like every one has the 3 prong with the inter lock. Sweet set up David and Bill. You all gave me so much info. I wish I would have asked for help or advice first. Thanks again you wise Men. πŸ‘Š πŸ‘Š πŸ‘Š πŸ™ πŸ™ πŸ™ ;)
The 4 prong on that generator is for combination 120/240 Volts @ 30 Amperes. The 3 prong is for 120 Volts only @ 30 Amperes.

The inlet in the photo in my previous post was a twist lock combination 120/240 Volt @ 50 Amperes.
 
Last edited:
Yeah I want it done correctly for sure. I noticed the 30 amp 4 prong and a 30 amp 3 prong coming off the generator so i asked for that 4 prong set up. But it looks like every one has the 3 prong with the inter lock. Sweet set up David and Bill. You all gave me so much info. I wish I would have asked for help or advice first. Thanks again you wise Men. πŸ‘Š πŸ‘Š πŸ‘Š πŸ™ πŸ™ πŸ™ ;)
Donny,
All is good Brother! The more we ALL learn the better life is! We ALL pass it forward! πŸ‘πŸ»πŸ‘ŠπŸ»πŸ‘ŠπŸ»πŸ‘ŠπŸ»πŸ‘πŸ»πŸ˜‰
 
Nice @Iron Man !

After being without power over the course of a week during Winter Storm Uri, decided to have a transfer switch put in when I built my new shop this summer.

Im getting gas routed to the house and will also supply the shop, I might get a LP Kohler or Generac later but for now grabbed a Westinghouse Wgen9500. Should get me by if power goes out for an extended time.

Moved my meter to the shop so know transfer switch is before shop and house. (not in the image but I have a 50 amp gen cord coming out of the transfer switch now)